        <title>Siltumsūkņu salīdzināšana</title>
        <description>Cenšos salīdzināt gaiss/ūdens SS, Nibe ar Daikin, bet netieku gudrs, kuram labāki COP, jo NIBE norādīts COP, savukārt Daikinam SCOP.

NIBE COP`i:
https://i.imgur.com/gDXSzbH.jpg

Daikin:
https://i.imgur.com/8ZpYs3W.jpg


Varbūt kāds var palīdzēt saprast šito maģiju par SS?

Paldies


P.S. Vispār smadzenes var izmežģīt ar tiem COP/SCOP/EER.</description>
        <link>https://building.lv/forums/99/211021/211021/_subject_#msg-211021</link>
        <lastBuildDate>Wed, 15 Apr 2026 04:34:49 +0300</lastBuildDate>
        <generator>Phorum 5.2.23</generator>
        <item>
            <guid>https://building.lv/forums/99/211021/220451/_subject_#msg-220451</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/220451/_subject_#msg-220451</link>
            <description><![CDATA[ KārlisG rakstīja:<br />
-------------------------------------------------------<br />
&gt; Vai mūsu plātuma grādos ir kāds vismaz relatīvi<br />
&gt; neatkarīgs konsultants/speciālists, kuram var<br />
&gt; godīgi samaksāt un tikt pie racionālām<br />
&gt; rekomendācijām? Aldiss- kā ar Jums? :)<br />
&gt; <br />
&gt; <br />
&gt; Kāds viedoklis par Stiebel eltron (<br />
&gt; [<a href="https://www.stiebel-eltron.com/en/home/products-solutions/renewables/heat_pump/air-water_heat_pumps.html"  rel="nofollow">www.stiebel-eltron.com</a>]<br />
&gt; ) piedāvātajiem gaiss-ūdens SS?<br />
<br />
Neesmu nekāds mācīts speciālists par siltumsūkņiem, tik vien kā savām rociņām pārvietojis kroga maksātnespējas ietvaros pa ūtrupes cenām iegādāto  aparātu uz savām mājām. Pluss arī palīdzējis dažiem saviem radiniekiem ar SS. <br />
<br />
Ideāls aparāts manā skatījumā vēl nav  uzbūvēts, bet, ja nu izvēle ir kritusi pa labu gaiss-ūdens siltumsūknim (un kāda tam motivācija), tad vispirms   jātiek skaidrībā, kādas ir vajadzības. <br />
Vai tā ir esošā māja, projektēšanā, būvniecības sākumā vai noslēgumā esoša, cik labi ir vai būs nosiltināta (subjektīvi) , kāda platība, siltās grīdas un/vai radiatori,tikai apkurei vai arī karstajam ūdenim, cik m3 karstā ūdens patērētu mēnesī, uz kuru debess pusi būs novietots SS. <br />
Tad vēl pieejamā elektrotīkla jauda un fāžu skaits.]]></description>
            <dc:creator>Aldiss</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Fri, 16 Jul 2021 17:38:23 +0300</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/220450/_subject_#msg-220450</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/220450/_subject_#msg-220450</link>
            <description><![CDATA[ Vai mūsu plātuma grādos ir kāds vismaz relatīvi neatkarīgs konsultants/speciālists, kuram var godīgi samaksāt un tikt pie racionālām rekomendācijām? Aldiss- kā ar Jums? :)<br />
<br />
<br />
Kāds viedoklis par Stiebel eltron ( [<a href="https://www.stiebel-eltron.com/en/home/products-solutions/renewables/heat_pump/air-water_heat_pumps.html"  rel="nofollow">www.stiebel-eltron.com</a>] ) piedāvātajiem gaiss-ūdens SS?]]></description>
            <dc:creator>KārlisG</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Fri, 16 Jul 2021 16:26:12 +0300</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/219088/_subject_#msg-219088</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/219088/_subject_#msg-219088</link>
            <description><![CDATA[ &gt;&gt;<br />
Kompresors neieslēdzās pretējā virzienā -nemaina griešanās virzienu , tas ir redzams ražotāja manuāļa sadaļā -Principle of operation&gt;&gt;&gt;<br />
<br />
Izlasi vēlreiz rakstīto. Nav  stāsts par kompresoru. Siltumsūkņi ar āra hidromoduli, pie - 20 grādiem, kad ieslēdzas tens, turpina sūknēt ūdeni uz āra moduli, kur siltuma zudumi ir oi-oi cik lieli. Tā 2cm izolācija uz caurulēm diži daudz nenoizolē, uz termogrāfa izskatās briesmīgi.<br />
T.i, siltumsūknis nepiedalās sildīšanā (kompresors vairs neslēdzas iekšā), bet gan dzesēšanā. Augstāk rakstītais neattiecas uz split sistēmām, kur starp iekšas un āra moduli cirkulē freons.]]></description>
            <dc:creator>Aldiss</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sun, 07 Mar 2021 22:37:39 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/219087/_subject_#msg-219087</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/219087/_subject_#msg-219087</link>
            <description><![CDATA[ Aldiss rakstīja:<br />
-------------------------------------------------------<br />
&gt; Rainis rakstīja:<br />
&gt; -------------------------------------------------------<br />
&gt; &gt; Aldi,<br />
&gt; &gt;<br />
&gt; &gt; Vai reāli ir kas labāks/efektīvāks par Nibe<br />
&gt; F2120,<br />
&gt; &gt; 12kw 3 fāzes? Vēl neko neesmu atradis (cik esmu<br />
&gt; &gt; izpratis viņus un māku salīdzināt).<br />
&gt; &gt;<br />
&gt; &gt; Sākot no 19 lpp ir visi teh. parametri:<br />
&gt; &gt;<br />
&gt; [<a href="https://www.nibe.lv/nibedocuments/26759/M11996-5.pdf"  rel="nofollow">www.nibe.lv</a>]<br />
&gt; <br />
&gt; NIBE F2120 ir labs aparāts, bet, kā jau katram<br />
&gt; ražojumam ir savas dīvainības. Tā kā Eiropas<br />
&gt; normatīvi COP aprēķinos neiekļauj atkausēšanai<br />
&gt; patērēto enerģiju, tad lielākās atšķirības starp<br />
&gt; ražotājiem ir tieši ar to.<br />
&gt; <br />
&gt; Atkausēšana Nibe tiek ieslēgta pamatojoties tikai<br />
&gt; uz viena informācijas avota- āra moduļa radiatora<br />
&gt; temperatūras devēja datiem un laika periodu x, cik<br />
&gt; ilgi strādājis negatīvā temperatūrā. Ja gaisa<br />
&gt; apkārtējā gaisa t ir lielāka par plus 4 grādi,<br />
&gt; izmanto pasīvo atkausēšanu- izslēdzas kompresors,<br />
&gt; bet ventilators paliek ieslēgts. Ja gaisa t ir<br />
&gt; zemāka par plus 4, tad savukārt izslēdzas<br />
&gt; ventilators un kompresors ieslēdzas pretējā<br />
&gt; virzienā- tiek saldēts no ēkas saņemtais ūdens un<br />
&gt; karsēts āra moduļa radiators. Tam sasniedzot<br />
&gt; pozitīvu temperatūru Y, atkausēšana izbeidzas.<br />
&gt; Ja Google nemelo, tad pie negatīvām temperatūrām<br />
&gt; Daikin vienkārši ik pēc 25 minūtēm uz brīdi<br />
&gt; ieslēdz reversu virzienu un uzsāk atkausēšanu.<br />
&gt; T.i, atkausēšana gan Nibe,gan Daikin tiek ieslēgta<br />
&gt; neatkrīgi no tā,ir vai nav apledojums un cik biezs<br />
&gt; tas ir.<br />
&gt; <br />
&gt; Panasonic bez temperatūras devējiem izmanto arī<br />
&gt; kompresora jaudas zudumu mērījumus ciklā, tādejādi<br />
&gt; atkausēšanu vairāk vai mazāk piemērojot reālajai<br />
&gt; nepieciešamībai, kas Latvijas mainīgajā klimatā<br />
&gt; varētu būt noderīgi.<br />
&gt; <br />
&gt; Vairumam siltumsūkņiem bez &quot;split&quot; ir viena<br />
&gt; īpanība- ja ēkā ir sasniegta nepieciešamā t un<br />
&gt; kompresors nestrādā, tik un tā caur āra moduli no<br />
&gt; ēkas un atpakaļ tiek dzenāts situmnesējs.  19mm<br />
&gt; bieza siltumiolācija uz 60 grādu siltām caurulēm<br />
&gt; mani diez ko nepārliecina. Siltumsūknis faktiski<br />
&gt; kļūst par aukstumsūkni. Iespējams,tas tiek darīts<br />
&gt; baidoties no sasalšanas- Itālijā nez vai kāds<br />
&gt; sistēmai pievieno glikolu, kas pie mums ir<br />
&gt; obligāts pasākums.<br />
<br />
Kompresors neieslēdzās pretējā virzienā -nemaina griešanās virzienu , tas ir redzams ražotāja manuāļa sadaļā -Principle of operation]]></description>
            <dc:creator>JJ</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sun, 07 Mar 2021 18:47:56 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211293/_subject_#msg-211293</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211293/_subject_#msg-211293</link>
            <description><![CDATA[ Martinz77 rakstīja:<br />
-------------------------------------------------------<br />
&gt; Kam ir kadas atsauksmes par siltumsuknis.lv vini<br />
&gt; tak ari sola A+++efektivitati. Pie minus25<br />
<br />
Iesaku pārlasīt manu postu 29/12/2019 04:59<br />
<br />
Skatamies gaiss-ūdens SS, piemēram,<br />
[<a href="https://www.siltumsuknis.lv/gaisa-udens-siltumsuknis-daikin-altherma-3/"  rel="nofollow">www.siltumsuknis.lv</a>]<br />
<br />
Detalizēta informācija pieejama katalogā [<a href="https://siltumsuknis.lv/wp-content/uploads/2018/08/Daikin-Altherma-3-product-catalogue-ECPEN18-786.pdf"  rel="nofollow">siltumsuknis.lv</a>]<br />
<br />
A tur SCOPi priekš average climate, bet mēs esam  cold climate zona. Tāpat pie zemām temperatūrām ir vērojams būtisks siltumjaudas kritums, salīdzinot ar nominālo. Jā, piesildīs ar elektrību iztrūkumu. Efektivitāte rēķināta, neņemot vērā elektrisko piesildi, kura varētu būt vajadzīga, kā arī visticamāk defrost zudumi nav ņemti vērā.<br />
<br />
Prasi pārdevējiem informāciju, kas attiecas uz LV. Pircējam jābūt skaidrībai, ka viņa mājai ar noteikto energoefektivitāti (siltumzudumi zināmi pie konkrētām temperatūrām)  aptuveni N stundas gadā siltumsūknis piesildīs ar elektrību tik un tik kWh. Tas būs atkarīgs no tā, kur māja atrodas, piemēram, Liepājā būs  siltāks nekā Zosēnos, attiecīgi mazāk laika gaiss-ūdens SS darbojas nelabvēlīgos apstākļos.]]></description>
            <dc:creator>Ambrosio</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Fri, 03 Jan 2020 18:04:09 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211272/_subject_#msg-211272</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211272/_subject_#msg-211272</link>
            <description><![CDATA[ Martinz77, par kādu iet runa, gaiss-gaiss vai gaiss-ūdens ?]]></description>
            <dc:creator>Rainis</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Fri, 03 Jan 2020 10:45:23 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211271/_subject_#msg-211271</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211271/_subject_#msg-211271</link>
            <description><![CDATA[ Tikai ne gaisa ss pilnvērtīgai apkurei - zem +4 sanāk tīra kurināšana ar elektrību. Pieredze darbā ilgus gadus.<br />
Tikai zemes.]]></description>
            <dc:creator>aaaa</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Fri, 03 Jan 2020 10:32:42 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211265/_subject_#msg-211265</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211265/_subject_#msg-211265</link>
            <description><![CDATA[ Kam ir kadas atsauksmes par siltumsuknis.lv vini tak ari sola A+++efektivitati. Pie minus25]]></description>
            <dc:creator>Martinz77</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Fri, 03 Jan 2020 09:26:34 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211232/_subject_#msg-211232</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211232/_subject_#msg-211232</link>
            <description><![CDATA[ daudzjautajumi rakstīja:<br />
-------------------------------------------------------<br />
&gt; es arī par gaiss ūdens domāju, jaunbūve pēc ubakus<br />
&gt; heat demand calculatora kā lokāciju ielikot davos,<br />
&gt; kas ir  grādu ziņā lidzīga mums sanāk apkures<br />
&gt; katla jauda 6kw vajadzīga,  1 st 200kvm siltās<br />
&gt; grīdas visur, nu un  rtb  granulu katls sanāk<br />
&gt; principā nenozīmīgi lētāk siltumsūkni, bet tad<br />
&gt; jākrāmē tās granulas, jādomā kur to glabāt utt kur<br />
&gt; tad tas profits sanāks ar tām granulām?&gt;<br />
<br />
Granulu katls nu nekā nesanāk lētāk par gss.]]></description>
            <dc:creator>Ahaas</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Thu, 02 Jan 2020 08:30:36 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211231/_subject_#msg-211231</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211231/_subject_#msg-211231</link>
            <description><![CDATA[ daudzjautājumi<br />
Lai būtu papildus viela pārdomām, tad Liepāja, Jēkabpils un Rēzekne ir gandrīz vienos platuma grādos. Priekš  siltumsūkņa, kas  siltumu ņem no gaisa, diezgan atšķirīgas vides dažādos griezumos un līdz ar to arī siltumsūkņa ekspluatācijā...]]></description>
            <dc:creator>ETT</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Wed, 01 Jan 2020 19:02:46 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211229/_subject_#msg-211229</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211229/_subject_#msg-211229</link>
            <description><![CDATA[ es arī par gaiss ūdens domāju, jaunbūve pēc ubakus heat demand calculatora kā lokāciju ielikot davos, kas ir  grādu ziņā lidzīga mums sanāk apkures katla jauda 6kw vajadzīga,  1 st 200kvm siltās grīdas visur, nu un  rtb  granulu katls sanāk principā nenozīmīgi lētāk siltumsūkni, bet tad jākrāmē tās granulas, jādomā kur to glabāt utt kur tad tas profits sanāks ar tām granulām?&gt;]]></description>
            <dc:creator>daudzjautajumi</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Wed, 01 Jan 2020 16:51:15 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211148/_subject_#msg-211148</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211148/_subject_#msg-211148</link>
            <description><![CDATA[ Ja kas, tad gaisa siltumsūkņa perspektivitāti var balstīt uz zinātniski dokumentētiem pamatiem.  Atliek tikai noticēt.    [<a href="https://www4.meteo.lv/klimatariks/"  rel="nofollow">www4.meteo.lv</a>]<br />
Eeeehhh. Nespīd vairs nedēļām gari hokeja turnīri uz vietējā dīķīša kā 70-ajos.]]></description>
            <dc:creator>SerViss</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sun, 29 Dec 2019 15:53:14 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211143/_subject_#msg-211143</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211143/_subject_#msg-211143</link>
            <description><![CDATA[ siltumsuknis.lv Jums pielies pilnas ausis par A+++ efektivitati]]></description>
            <dc:creator>pip</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sun, 29 Dec 2019 13:59:29 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211138/_subject_#msg-211138</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211138/_subject_#msg-211138</link>
            <description><![CDATA[ Latvijā nenorāda, bet esmu atradis Panasonic 389 lpp katalogu 2091-2020 gadam, kur ir norādīts daudz teh. informācijas par katru sūkni.]]></description>
            <dc:creator>Rainis</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sun, 29 Dec 2019 09:19:13 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211136/_subject_#msg-211136</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211136/_subject_#msg-211136</link>
            <description><![CDATA[ Noderīgs un pētījums interesentiem par gaiss-ūdens siltumsūkņiem, kas nenāk no ražotājiem vai pārdevējiem, varētu būt šis:<br />
Nordic Council of Ministers. NORDSYN STUDY ON AIR-TO-WATER HEAT PUMPS IN HUMID NORDIC CLIMATE. [<a href="https://norden.diva-portal.org/smash/get/diva2:1312951/FULLTEXT01.pdf"  rel="nofollow">norden.diva-portal.org</a>]<br />
<br />
Daži secinājumi:<br />
<br />
* Latvija ir aukstā klimata joslā, bet norādīt performance ir obligāti tikai vidēja klimata joslai. Interesējoties pie pārdevējiem, tam jāpievērš īpaša uzmanība. For different types of heat pumps and package products, the energy labels display different information, it is usually  mandatory  to  indicate  information  for  average  climate  conditions,  but  for colder climate conditions it is either optional or less information on the label.<br />
<br />
* Lai arī pētījumā nav pārstāvēeti pēdējo gadu modeļi, uzlabojumi efektivitātē nebūs revolucionāri, ja 13 gadu laikā COP ir uzlabots tikai par 15%. On average the COP increased about 15% from the first test in 1999 until the later test in 2012. <br />
<br />
* Testēšanas standarts atļauj testēšanu pie relatīvi zemāka mitruma nekā pie mums, bet pie lielāka relatīva mitruma, defrosts būs biežāk. The efficiency (COP) of an air-to-water heat pump depends on the outdoor climate, both temperature and humidity. <br />
<br />
* Defrosts var paņemt jūtamu daļu no saražotā siltuma. Ja jau vidēja klimata UK un DE, tas ir vismaz 10%. Four air-to-water heat pumps in the UK and in Germany are investigated in detail on defrosting showing around 10% of total heat output is used for defrosting. Compared to similar results from other heat pumps in the UK, these ratios of defrosting energy to total energy from the heat pumps are much higher. <br />
<br />
* Ražotāji efektivitāti parasti norāda sev izdevīgākā gaismā - pie zemas ssiltumjaudas, kad nevajag ierēkināt  sildītāju. Atceramis no šīs diskusijas, ka pie zemām temperatūrām, kad mājai vajag vairāk siltuma, SS var ražot mazāk nekā nominālā siltumjauda. Most  air-to-water  heat  pumps  investigated  through  browsing  marketing  data  are declared for a relatively low heating capacity (a low value of Pdesign). This means that they are declared to operate without any backup heater for most, or in some cases all, hours of the year in the SCOP bin calculation<br />
<br />
* Kā šmugulēejas daži &quot;krāniņi&quot; - One  manufacturer  is  not  presenting  any  SCOP  values  at  all,  the  values  in  the diagrams  below  are  calculated  from  the  ηs  values  in  their  data  sheets.  The  two manufacturers  of  split  heat  pumps  are  not  presenting  any  data  at  all  for  the  Cold climate, despite the information is taken from their Swedish site. One of them is only presenting  information  for  the  Average  climate  and  the  low  temperature  heating system. <br />
<br />
* Atkal defrosts, no kura var pamanīties izvairīties efektivitātes testos. The test period in the standards are not long enough to include a defrost period It has been seen in EN14825 and EN14511 tests performed at RISE on air-to-water from European heat pumps that all recently tested heat pumps are designed to handle the test  cycles  without  need  to  defrost  within  the  evaluation  period.  However,  when measuring the heat pumps during a longer period, the heat pumps needed to defrost. Figure 43 shows the difference in COP of measurement on seven different heat pumps when no defrost period is included in the cycle compared to when it is included. The results show that excluding the defrost means in most cases COP that are 6–11% higher compared to including the defrost. <br />
<br />
* Since several of the lowest performing heat pumps from the field can be found in countries with high air humidity, differences in frosting and defrosting of the outdoor heat exchanger surfaces could be an explanation to the low reported SPF values.<br />
<br />
* Uzstādīšanas un konfigurēšanas kļūdas arī var samazināt efektivitāti. Temperatūras režīms - pats par sevi.<br />
<br />
* Ražotājiem un pārdevējiem ir tendence plātīties ar efektivitātes skaitļiem vidējam klimatam, nepaskaidrojot, ka tiem nav nekāda sakara ar auksto klimatu (Latviju):<br />
<br />
One manufacturer is actually using the very high SCOP value for the Average climate in their marketing on the Swedish marketing: “With a SCOP exceeding 5,0* the heat pump is delivering more than five times as much heat compared to an electric boiler with the same electric consumption.” The explanation of the * is not found on the site itself, but the product sheet (pdf) needs to be opened to see it. The explanation reads: “...has a SCOP&gt;5,0 (Average climate, Low temperature) and a SCOP of 4,3 (Cold climate, Low temperature) according to European standard...”That the average climate is not relevant in Sweden is not explained, given the consumer basically incorrect information. Other manufacturers are presenting SCOP values for both for the Average and the Cold  climate  in  the  product  sheets,  but  without  any  explanation  that  the  Average climate is not relevant in Sweden.  <br />
<br />
Vai kāds var pateikt, kuri pārdevēji Latvijā SS norāda SCOP aukstajam klimatam uzreiz produkta web lapā, nevis kaut kur ellē ratā kādā pdfā? Pašam vairs negribas meklēt un apkopot šādu informāciju.]]></description>
            <dc:creator>Ambrosio</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sun, 29 Dec 2019 04:59:52 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211135/_subject_#msg-211135</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211135/_subject_#msg-211135</link>
            <description><![CDATA[ Tev ir T-CAP vai High Performance?]]></description>
            <dc:creator>Rainis</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sun, 29 Dec 2019 02:41:11 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211134/_subject_#msg-211134</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211134/_subject_#msg-211134</link>
            <description><![CDATA[ Man pašam ir Panasonic AQUAREA. Iegādājos to viena kroga maksātnespējas ietvaros &quot;pa kapeikām&quot;. Pats noskrūvēju, pārvedu un kopš pagājušā gada novembra izmamtoju sev. Liels sals nav pieredzēts, rezervei ir saglabājušās krāsnis, kuras pagājušajā sezonā iekurināju dažas reizes. Šoruden vēl neesmu kurinājis.<br />
Temperatūrai esot ap nulli, defrost ir apmēram reizi divās stundās.]]></description>
            <dc:creator>Aldiss</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sun, 29 Dec 2019 00:06:19 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211132/_subject_#msg-211132</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211132/_subject_#msg-211132</link>
            <description><![CDATA[ Es protams atainojos visiem Daikin SS pārdevējiem, bet tā nu tolaik sanāca ,  ka, vinnējot &quot;melnā humora top&quot; izlozē  Radio swh vinnēju siltumsūkni Daikin. Bet sakarā ar to, ka šajā forumā palasījos, ka ne viss ir tas ko mums mēģina iesmērēt, Tas siltumsūknis tomēr vair[āk ir kondicionieris :) Vairs neatceros par cik mazāk, bet mabn liekas par 50 % mazāk, tās kastes tomēr pārdevu... Nav jau nekādas šķrobes pret radio, kas rekllāmas nolūkos... bet tomēr...]]></description>
            <dc:creator>ETT</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sat, 28 Dec 2019 22:11:13 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211131/_subject_#msg-211131</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211131/_subject_#msg-211131</link>
            <description><![CDATA[ Aldiss rakstīja:<br />
-------------------------------------------------------<br />
&gt; Atradu rakstu, kas bija par iemeslu, kāpēc pirms<br />
&gt; gada  nenopirku Daikin SS.<br />
&gt; <br />
&gt; [<a href="https://lamiacasaelettrica.com/daikin-defrost-a-conscious-choice/"  rel="nofollow">lamiacasaelettrica.com</a>]<br />
<br />
Labs materiāls.<br />
<br />
&quot;Unfortunately winter defrosts are not a neglible factor and can lead to unpleasant surprises. If the choice is not conscious.&quot;<br />
<br />
Ja kāds gaiss-ūdens SS pārdevējs slēpj to,  ka un par cik defrrosts samazina efektivitāti, var uzreiz &quot;dot bietē&quot;, tas ir, pagriezties un iet projām :)]]></description>
            <dc:creator>Ambrosio</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sat, 28 Dec 2019 17:30:27 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211128/_subject_#msg-211128</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211128/_subject_#msg-211128</link>
            <description><![CDATA[ Aldi, tev ir Ecodan/Zubadan ?]]></description>
            <dc:creator>Rainis</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sat, 28 Dec 2019 14:33:56 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211120/_subject_#msg-211120</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211120/_subject_#msg-211120</link>
            <description><![CDATA[ Atradu rakstu, kas bija par iemeslu, kāpēc pirms gada  nenopirku Daikin SS.<br />
<br />
<br />
[<a href="https://lamiacasaelettrica.com/daikin-defrost-a-conscious-choice/"  rel="nofollow">lamiacasaelettrica.com</a>]]]></description>
            <dc:creator>Aldiss</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sat, 28 Dec 2019 11:23:57 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211118/_subject_#msg-211118</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211118/_subject_#msg-211118</link>
            <description><![CDATA[ Tinis rakstīja:<br />
-------------------------------------------------------<br />
&gt; Elektrības patēriņu var izrēķināt. Jāzin cik kWh<br />
&gt; siltuma patērē māja pie nulle grādiem un<br />
&gt; siltumsūkņa COP pie nulle grādiem.<br />
<br />
Elektrības patēriņa rēķināšana būs tikai pieņēmums.<br />
Siltumsūkūkņa reālais COP var būt (visbiežāk ir) krietni atšķirīgs no deklarētā, jo deklarētais neietver sevī atkausēšanai patērēto siltumenerģiju.<br />
Arī laika apstākļi, siltumsūkņa novierojums saules vai ēnas pusē pie ziemeļu/dienvidu sienas ietekmēs patēriņu. Bezvēja laikā pie vienas un tās pašas 0 temperatūras SS atkausēšai vajag krietni mazāk siltuma un laika nekā stiprā vējā. <br />
 Daļu no laika sitlumssūknis strāds ekonomiskajā zemo temperatūru režīmā tikai uz siltajām grīdām,bet daļu no laika- augstajās temperatūrās karstā ūdens sagatavošanai + grīdām tiks uzmaisīta pareizā t no karstās cilpas. COPi abiem režīmiem ir atšķirīgi.]]></description>
            <dc:creator>Aldiss</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sat, 28 Dec 2019 11:03:24 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211117/_subject_#msg-211117</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211117/_subject_#msg-211117</link>
            <description><![CDATA[ Elektrības patēriņu var izrēķināt. Jāzin cik kWh siltuma patērē māja pie nulle grādiem un siltumsūkņa COP pie nulle grādiem.]]></description>
            <dc:creator>Tinis</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sat, 28 Dec 2019 10:13:26 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211116/_subject_#msg-211116</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211116/_subject_#msg-211116</link>
            <description><![CDATA[ Elektrības patēriņš dienā ir nezināmais lielums, prasi pārdevējam un pareizini viņa nosaukto ciparu ar 2. <br />
Mans rēķins slikti siltinātai mājai novembrī ir par 56 eur lielāks kā jūnijā.<br />
<br />
Gaiss ūdens SS gala rezultātu ļooooti ietekmē tas, vai,cik daudz un cik bieži tiek izmantots siltais ūdens. Kamēr vien tiek sildīts siltais ūdens, visa SS sistēma strādā uz 55 grādi,grīdām 30 grādīgais tiek ražots/uzjaukts no 55.]]></description>
            <dc:creator>Aldiss</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sat, 28 Dec 2019 09:19:36 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211114/_subject_#msg-211114</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211114/_subject_#msg-211114</link>
            <description><![CDATA[ Man interesētu cik vajadzētu būt kwh dienā uz 120m2 pie 0 gradiem  siltināta un slikti siltinata ēka. siltas gridas. Iekseja temperatura 18 gradi vai 25 turpgaitas temp. Kkur var kko tadu uzzinat.]]></description>
            <dc:creator>pip</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sat, 28 Dec 2019 02:32:29 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211113/_subject_#msg-211113</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211113/_subject_#msg-211113</link>
            <description><![CDATA[ Ko nozīmē bez &quot;split&quot;?.<br />
Pareizāk būtu bijis lietot &quot;ar Monoblock&quot;.<br />
<br />
Ražotājiem ir dažādas terminolģijas, bet vispārīgi gaisa Ss var iedalīt divās grupās- Monoblock (kur iztvaikotājs,kompresors un situma ražošana notiek āra modulī) un Split (kur iztvaikotājs ir āra modulī, bet kompresors un situma ražošana atrodas iekštelpās). Āra Monoblock savienojums ar iekštelpās esošo kontrolieri/sūkņiem ir ar prāvām karstā ūdens caurulēm, bet Split abi moduļi ir svienoti ar tievām freona caurulītēm.<br />
NIBE F2120 ir monobloc,Nibe Split ir Split.<br />
Panasonic ar Monoblock apzīmē modeli, kurā arī siltā ūdens boileris ir ārtelpās.]]></description>
            <dc:creator>Aldiss</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Sat, 28 Dec 2019 00:49:07 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211109/_subject_#msg-211109</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211109/_subject_#msg-211109</link>
            <description><![CDATA[ Aldiss rakstīja:<br />
<br />
&gt; Vairumam siltumsūkņiem bez &quot;split&quot; ir viena<br />
&gt; īpanība- ja ēkā ir sasniegta nepieciešamā t un<br />
&gt; kompresors nestrādā, tik un tā caur āra moduli no<br />
&gt; ēkas un atpakaļ tiek dzenāts situmnesējs.  19mm<br />
&gt; bieza siltumiolācija uz 60 grādu siltām caurulēm<br />
&gt; mani diez ko nepārliecina. Siltumsūknis faktiski<br />
&gt; kļūst par aukstumsūkni. Iespējams,tas tiek darīts<br />
&gt; baidoties no sasalšanas- Itālijā nez vai kāds<br />
&gt; sistēmai pievieno glikolu, kas pie mums ir<br />
&gt; obligāts pasākums.<br />
<br />
Ko nozīmē bez &quot;split&quot;?]]></description>
            <dc:creator>Proktologs.</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Fri, 27 Dec 2019 22:09:51 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211106/_subject_#msg-211106</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211106/_subject_#msg-211106</link>
            <description><![CDATA[ Rainis rakstīja:<br />
-------------------------------------------------------<br />
&gt; Aldi,<br />
&gt; <br />
&gt; Vai reāli ir kas labāks/efektīvāks par Nibe F2120,<br />
&gt; 12kw 3 fāzes? Vēl neko neesmu atradis (cik esmu<br />
&gt; izpratis viņus un māku salīdzināt).<br />
&gt; <br />
&gt; Sākot no 19 lpp ir visi teh. parametri:<br />
&gt; [<a href="https://www.nibe.lv/nibedocuments/26759/M11996-5.pdf"  rel="nofollow">www.nibe.lv</a>]<br />
<br />
NIBE F2120 ir labs aparāts, bet, kā jau katram ražojumam ir savas dīvainības. Tā kā Eiropas normatīvi COP aprēķinos neiekļauj atkausēšanai patērēto enerģiju, tad lielākās atšķirības starp ražotājiem ir tieši ar to. <br />
<br />
Atkausēšana Nibe tiek ieslēgta pamatojoties tikai uz viena informācijas avota- āra moduļa radiatora temperatūras devēja datiem un laika periodu x, cik ilgi strādājis negatīvā temperatūrā. Ja gaisa apkārtējā gaisa t ir lielāka par plus 4 grādi, izmanto pasīvo atkausēšanu- izslēdzas kompresors, bet ventilators paliek ieslēgts. Ja gaisa t ir zemāka par plus 4, tad savukārt izslēdzas ventilators un kompresors ieslēdzas pretējā virzienā- tiek saldēts no ēkas saņemtais ūdens un karsēts āra moduļa radiators. Tam sasniedzot pozitīvu temperatūru Y, atkausēšana izbeidzas.<br />
Ja Google nemelo, tad pie negatīvām temperatūrām Daikin vienkārši ik pēc 25 minūtēm uz brīdi ieslēdz reversu virzienu un uzsāk atkausēšanu.<br />
T.i, atkausēšana gan Nibe,gan Daikin tiek ieslēgta neatkrīgi no tā,ir vai nav apledojums un cik biezs tas ir.<br />
<br />
Panasonic bez temperatūras devējiem izmanto arī kompresora jaudas zudumu mērījumus ciklā, tādejādi atkausēšanu vairāk vai mazāk piemērojot reālajai nepieciešamībai, kas Latvijas mainīgajā klimatā varētu būt noderīgi.<br />
<br />
Vairumam siltumsūkņiem bez &quot;split&quot; ir viena īpanība- ja ēkā ir sasniegta nepieciešamā t un kompresors nestrādā, tik un tā caur āra moduli no ēkas un atpakaļ tiek dzenāts situmnesējs.  19mm bieza siltumiolācija uz 60 grādu siltām caurulēm mani diez ko nepārliecina. Siltumsūknis faktiski kļūst par aukstumsūkni. Iespējams,tas tiek darīts baidoties no sasalšanas- Itālijā nez vai kāds sistēmai pievieno glikolu, kas pie mums ir obligāts pasākums.]]></description>
            <dc:creator>Aldiss</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Fri, 27 Dec 2019 18:46:33 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211093/_subject_#msg-211093</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211093/_subject_#msg-211093</link>
            <description><![CDATA[ Ambrosio rakstīja:<br />
&gt; Pa stundā temperatūras grafiks droši vien nebūs atrodams,<br />
&gt; bet min max temperatūra konkrētā mēneša dienā gan<br />
&gt; ir pieejama, tad no tā var uztaisīt aptuvenu<br />
&gt; diennakts temperatūras svārtību grafiku pa  stundām.<br />
<br />
Labojums: LVĢMC var bez maksas dabūt klimata datus (temperatūru, mitrumu u.c.) pa stundām dažādās novērošanas stacijās - [<a href="https://www.meteo.lv/meteorologija-datu-meklesana/?nid=461"  rel="nofollow">www.meteo.lv</a>]]]></description>
            <dc:creator>Ambrosio</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Thu, 26 Dec 2019 18:07:26 +0200</pubDate>
        </item>
        <item>
            <guid>https://building.lv/forums/99/211021/211092/_subject_#msg-211092</guid>
            <title>Re: Siltumsūkņu salīdzināšana</title>
            <link>https://building.lv/forums/99/211021/211092/_subject_#msg-211092</link>
            <description><![CDATA[ Rodas sajūta, ka ražotāji speciāli tik ļoti visu sarežģījuši, lai mirstīgais cilvēks netiktu skaidrībā :)]]></description>
            <dc:creator>Rainis</dc:creator>
            <category>Inženiertīkli</category>
            <pubDate>Thu, 26 Dec 2019 18:04:38 +0200</pubDate>
        </item>